Hi JM,
It is possible to build the cable that you need, however we can’t suggest a pinout without knowing how the connector on the PLC is wired. In your support portal case we posted a diagram showing how the DB9 on the CDP is wired. You will need to have the same information for the connector on the PLC to determine the correct pinout for the cable.
The serial interface on the CDP is a DCE device with standard pin assignments. If the PLC also has a standard DCE interface you can use what’s called a ‘null modem’ or ‘crossover’ cable. If the PLC is a standard DTE interface you can use a ‘straight’ cable (pin 1 wired to pin 1, pin 2 wired to pin 2, etc…). Both of these types of cables you should be able to buy pre-made. If the PLC uses non-standard pin assignments you are more likely to need to build your own cable.